Havex, It’s Down With OPC

FireEye recently analyzed the capabilities of a variant of Havex
  (referred to by FireEye as “Fertger” or “PEACEPIPE”), the first
  publicized malware reported to actively scan OPC servers used for
  controlling SCADA (Supervisory Control and Data Acquisition) devices
  in critical infrastructure (e.g., water and electric utilities),
  energy, and manufacturing sectors.


 

While Havex itself is a somewhat simple PHP Remote Access Trojan
  (RAT) that has been analyzed by other sources, none of these have
  covered the scanning functionality that could impact     href="/content/fireeye-www/en_US/solutions/industrial-systems-and-critical-infrastructure-security.html">SCADA
    devices and other industrial control systems (ICS).
  Specifically, this Havex variant targets servers involved in OPC
  (Object linking and embedding for Process Control) communication, a
  client/server technology widely used in process control systems (for
  example, to control water pumps, turbines, tanks, etc.).


 


  Note: ICS is a general term that encompasses SCADA (Supervisory
    Control and Data Acquisition) systems, DCS (Distributed Control
    Systems), and other control system environments. The term SCADA is
    well-known to wider audiences, and throughout this article, ICS and
    SCADA will be used interchangeably.


 

Threat actors have leveraged Havex in attacks across the energy
  sector for over a year, but the full extent of industries and ICS
  systems affected by Havex is unknown. We decided to examine the OPC
  scanning component of Havex more closely, to better understand what
  happens when it’s executed and the possible implications.


 


  OPC Testing Environment


 

To conduct a true test of the Havex variant’s functionality, we
  constructed an OPC server test environment that fully replicates a
  typical OPC server setup (Figure 1
      [3]
). As shown, ICS or SCADA systems involve
  OPC client software that interacts directly with an OPC server, which
  works in tandem with the PLC (Programmable Logic Controller) to
  control industrial hardware (such as a water pump, turbine, or tank).
  FireEye replicated both the hardware and software the OPC server setup
  (the components that appear within the dashed line on the right side
  of Figure 1).


 

 


 

 

 


            width="458" height="183"
        class="aligncenter  wp-image-5991 landscape-sm" alt="havex1"
  src="/content/dam/legacy/blog/2014/07/havex1.png" />


    Figure 1: Topology of typical OPC server setup

The
    components of our test environment are robust and comprehensive to
    the point that our system could be deployed in an environment to
    control actual SCADA devices. We utilized an Arduino Uno
        [1]
as the primary hardware platform,
    acting as the OPC server. The Arduino Uno is an ideal platform for
    developing an ICS test environment because of the low power
    requirements, a large number of libraries to make programming the
    microcontroller easier, serial communication over USB, and cheap
    cost. We leveraged the OPC Server and libraries from St4makers
        [2]
(as shown in Figure 2). This software
    is available for free to SCADA engineers to allow them to develop
    software to communicate information to and from SCADA devices.


   


            width="288" height="201"
        class="aligncenter  wp-image-5990 landscape-sm" alt="havex2"
  src="/content/dam/legacy/blog/2014/07/havex2.png" />


    Figure 2: OPC Server Setup

Using the OPC Server
    libraries allowed us to make the Arduino Uno act as a true,
    functioning OPC SCADA device (Figure 3).


            width="265" height="200"
        class=" wp-image-5989 aligncenter landscape-sm" alt="havex3"
  src="/content/dam/legacy/blog/2014/07/havex3.png" />


    Figure 3: Matrikon OPC Explorer showing Arduino OPC
  Server

We also used Matrikon’s OPC Explorer
        [1]
, which enables browsing between the
    Arduino OPC server and the Matrikon embedded simulation OPC server.
    In addition, the Explorer can be used to add certain data points to
    the SCADA device – in this case, the Arduino device.


            width="393" height="157"
        class="aligncenter  wp-image-5988 landscape-sm" alt="havex4"
  src="/content/dam/legacy/blog/2014/07/havex4.png" />


    Figure 4: Tags identified for OPC server

In the OPC
    testing environment, we created tags in order to simulate a true OPC
    server functioning. Tags, in relation to ICS devices, are single
    data points. For example: temperature, vibration, or fill level.
    Tags represent a single value monitored or controlled by the system
    at a single point in time.

With our test environment
    complete, we executed the malicious Havex “.dll" file and
    analyzed how Havex’s OPC scanning module might affect OPC servers it
    comes in contact with.


    Analysis

The particular Havex sample we looked at was
    a file named PE.dll (6bfc42f7cb1364ef0bfd749776ac6d38). When looking
    into the scanning functionality of the particular Havex sample, it
    directly scans for OPC servers, both on the server the sample was
    submitted on, and laterally, across the entire network.

    style="text-align: left;">The scanning process starts when the Havex
    downloader calls the runDll export function.  The OPC scanner module
    identifies potential OPC servers by using the Windows networking
    (WNet) functions.  Through recursive calls to WNetOpenEnum and
    WNetEnumResources, the scanner builds a list of all servers that are
    globally accessible through Windows networking.  The list of servers
    is then checked to determine if any of them host an interface to the
    Component Object Models (COM) listed below:

 

 


   

 


                href="/content/dam/legacy/blog/2014/07/Screen-Shot-2014-07-17-at-12.31.56-PM.png">          width="547" height="191"
          class="alignnone  wp-image-6030 landscape-med"
          alt="Screen Shot 2014-07-17 at 12.31.56 PM"
    src="/content/dam/legacy/blog/2014/07/Screen-Shot-2014-07-17-at-12.31.56-PM.png" />


   

 

 


    Figure 5: Relevant COM objects

Once OPC servers are
    identified, the following CLSIDs are used to determine the
    capabilities of the OPC server:


            href="/content/dam/legacy/blog/2014/07/Screen-Shot-2014-07-17-at-12.33.22-PM.png">        width="554" height="224"
        class="alignnone  wp-image-6031 landscape-med"
        alt="Screen Shot 2014-07-17 at 12.33.22 PM"
  src="/content/dam/legacy/blog/2014/07/Screen-Shot-2014-07-17-at-12.33.22-PM.png" />


   


                Figure 6: CLSIDs used to determine capabilities of
      the OPC server

When executing PE.dll, all of the OPC
    server data output is first saved as %TEMP%\[random].tmp.dat. The
    results of a capability scan of an OPC server is stored in
    %TEMP%\OPCServer[random].txt. Files are not encrypted or deleted
    once the scanning process is complete.

Once the scanning
    completes, the log is deleted and the contents are encrypted and
    stored into a file named %TEMP%\[random].tmp.yls.  The encryption
    process uses an RSA public key obtained from the PE resource TYU. 
    The RSA key is used to protect a randomly generated 168-bit 3DES key
    that is used to encrypt the contents of the log.

The TYU
    resource is BZip2 compressed and XORed with the string “1312312”.  A
    decoded configuration for 6BFC42F7CB1364EF0BFD749776AC6D38 is
    included in the figure below:


   
                href="/content/dam/legacy/blog/2014/07/Screen-Shot-2014-07-17-at-12.27.24-PM.png">          width="601" height="241"
          class=" wp-image-6029 alignleft landscape-med"
          alt="Screen Shot 2014-07-17 at 12.27.24 PM"
  src="/content/dam/legacy/blog/2014/07/Screen-Shot-2014-07-17-at-12.27.24-PM.png" />


   


    Figure 7: Sample decoded TYU resource

The
    4409de445240923e05c5fa6fb4204 value is believed to be an RSA key
    identifier. The AASp1… value is the Base64 encoded RSA key.

A
    sample encrypted log file (%TEMP%\[random].tmp.yls) is below.


 

 


   

 

 

 

 

 

 

 


   

 

 

 

 

 

      cellpadding="0" border="1">
       
         
            colspan="2">00000000  32 39 0a 66 00 66 00 30  00 30 00 66
            00 66 00 30 29.f.f.0.0.f.f.000000010  00 30 00 66 00 66 00
            30  00 30 00 66 00 66 00 30 .0.f.f.0.0.f.f.000000020  00 30
            00 66 00 66 00 30  00 30 00 66 00 66 00 30
            .0.f.f.0.0.f.f.000000030  00 30 00 66 00 66 00 30  00 30 00
            66 00 37 39 36 .0.f.f.0.0.f.79600000040  0a 31 32 38 0a 96
            26 cc  34 93 a5 4a 09 09 17 d3 .128..&.4..J....00000050 
            e0 bb 15 90 e8 5d cb 01  c0 33 c1 a4 41 72 5f a5
            .....]...3..Ar_.00000060  13 43 69 62 cf a3 80 e3  6f ce 2f
            95 d1 38 0f f2 .Cib....o./..8..00000070  56 b1 f9 5e 1d e1
            43 92  61 f8 60 1d 06 04 ad f9 V..^..C.a.`.....00000080  66
            98 1f eb e9 4c d3 cb  ee 4a 39 75 31 54 b8 02
            f....L...J9u1T..00000090  b5 b6 4a 3c e3 77 26 6d  93 b9 66
            45 4a 44 f7 a2 ..J<.w&m..fEJD..000000A0  08 6a 22 89
            b7 d3 72 d4  1f 8d b6 80 2b d2 99 5d
            .j"...r.....+..]000000B0  61 87 c1 0c 47 27 6a 61  fc
            c5 ee 41 a5 ae 89 c3 a...G'ja...A....000000C0  9e 00 54 b9
            46 b8 88 72  94 a3 95 c8 8e 5d fe 23
            ..T.F..r.....].#000000D0  2d fb 48 85 d5 31 c7 65  f1 c4 47
            75 6f 77 03 6b -.H..1.e..Guow.k

 

 

--Truncated--Probable Key
    Identifierff00ff00ff00ff00ff00ff00ff00fRSA Encrypted 3DES Key5A EB
    13 80 FE A6 B9 A9 8A 0F 41…The 3DES key will be the last 24 bytes of
    the decrypted result.3DES IV88 72  94 a3 95 c8 8e 5d3DES Encrypted
    Logfe 23 2d fb 48 85 d5 31 c7 65 f1…


    Figure 8: Sample encrypted .yls file


    Execution

When executing PE.dll against the Arduino
    OPC server, we observe interesting responses within the plaintext
  %TEMP%\[random].tmp.dat:

 


   

 


                href="/content/dam/legacy/blog/2014/07/Screen-Shot-2014-07-17-at-12.41.27-PM.png">          width="508" height="557"
          class="alignnone  wp-image-6032 portrait-med"
          alt="Screen Shot 2014-07-17 at 12.41.27 PM"
    src="/content/dam/legacy/blog/2014/07/Screen-Shot-2014-07-17-at-12.41.27-PM.png" />


   

 

 


    Figure 9: Sample scan log

The contents of the tmp.dat
    file are the results of the scan of the network devices, looking for
    OPC servers. These are not the in-depth results of the OPC servers
    themselves, and only perform the initial scanning.

The
    particular Havex sample in question also enumerates OPC tags and
    fully interrogates the OPC servers identified within
    %TEMP%\[random].tmp.dat. The particular fields queried are: server
    state, tag name, type, access, and id. The contents of a sample
    %TEMP%\OPCServer[random].txt can be found below:

 


   

 


                href="/content/dam/legacy/blog/2014/07/Screen-Shot-2014-07-17-at-12.43.48-PM.png">          width="514" height="470"
          class="alignnone  wp-image-6033 landscape-med"
          alt="Screen Shot 2014-07-17 at 12.43.48 PM"
    src="/content/dam/legacy/blog/2014/07/Screen-Shot-2014-07-17-at-12.43.48-PM.png" />


   

 

 


    Figure 10: Contents of OPCServer[Random].txt OPC
  interrogation

While we don’t have a particular case study
    to prove the attacker’s next steps, it is likely after these files
    are created and saved, they will be exfiltrated to a command and
    control server for further processing.


    Conclusion

Part of threat intelligence requires
    understanding all parts of a particular threat. This is why we took
    a closer look at the OPC functionality of this particular Havex
    variant.  We don’t have any case study showcasing why the OPC
    modules were included, and this is the first “in the wild” sample
    using OPC scanning. It is possible that these attackers could have
    used this malware as a testing ground for future utilization,
  however.

Since ICS networks typically don’t have a high-level
    of visibility into the environment, there are several ways to help
    minimize some of the risks associated with a threat like Havex.
    First, ICS environments need to have the ability to perform full
    packet capture ability. This gives incident responders and engineers
    better visibility should an incident occur.

Also, having
    mature incident processes for your ICS environment is important.
    Being able to have security engineers that also understand ICS
    environments during an incident is paramount. Finally, having
    trained professionals consistently perform security checks on ICS
    environments is helpful. This ensures standard sets of security
    protocols and best practices are followed within a highly secure
  environment.

We hope that this information will further educate
    industrial control systems owners and the security community about
    how the OPC functionality of this threat works and serves as the
    foundation for more investigation. Still, lots of questions remain
    about this component of Havex. What is the attack path? Who is
    behind it? What is their intention? We’re continuing to track this
    specific threat and will provide further updates as this new tactic
  unfolds.


    Acknowledgements

We would like to thank Josh Homan for
    his help and support.


    Related MD5s

ba8da708b8784afd36c44bb5f1f436bc


 

6bfc42f7cb1364ef0bfd749776ac6d38


 

4102f370aaf46629575daffbd5a0b3c9


 

  References

 

 

   

     


                  href="http://www.opcdatahub.com/WhatIsOPC.html">http://www.matrikonopc.com/products/opc-desktop-tools/opc-explorer.aspx

          http://arduino.cc/en/Main/arduinoBoardUno

          http://www.f-secure.com/weblog/archives/00002718.html

      http://www.opcdatahub.com/WhatIsOPC.html


Source: Havex, It’s Down With OPC